A Virtual Induction Machine (VIM)-based synchronizer is a control and synchronization strategy for grid-following Voltage Source Converters (VSCs) in electric power systems, primarily targeting operations in low-inertia grids. The VIM approach emulates the dynamic properties of a physical induction machine, notably self-synchronization, oscillation damping, and standalone capability, using only converter output voltage and current measurements. By directly inferring grid frequency, the VIM excises the need for a traditional Phase-Locked Loop (PLL) synchronizer and thereby enhances small- and large-signal stability, while retaining conventional outer and inner converter control architectures (Stanojev et al., 2021).
1. Induction Machine Emulation: Mathematical Foundations
The VIM methodology is found on a rigorous emulation of the dq-frame model of a squirrel-cage induction machine, rotating at unknown . The core stator and rotor equations are:
where , are stator/rotor resistances, , , are inductances, all refer to the synchronous reference frame, and (slip).
Adopting a standard field-oriented alignment (), and are algebraically eliminated. The slip, rotor dynamics, and electromagnetic torque equations simplify and support Laplace-domain transfer function derivations for robust controller synthesis. These relationships are central to the VIM structure (Stanojev et al., 2021).
2. Grid Frequency Recovery Without a PLL
The VIM synchronizer reconstructs the grid's synchronous speed by analogizing the converter’s filter-side voltage and current measurements (, ) to an induction machine stator. The estimation proceeds as:
- Slip estimation: Based on the measured stator currents,
- Rotor speed (“swing” equation):
- Synchronous speed:
where is an initialization, the emulated inertia, the damping constant, and the converter power.
By integrating (with the base frequency in radians/sec), the approach generates angle and speed references needed for transformation and current-regulation.
3. Index-1 Differential-Algebraic System Representation
The VIM synchronizer is mathematically compacted into an index-1 differential-algebraic equation (DAE) system, which is structurally suitable for small-signal and eigenvalue stability analyses:
Differential states include: Algebraic constraints incorporate current derivatives and frequency saturations: The state and algebraic partitioning enables systematic linearization, well-posedness, and integration with other converter or network models (Stanojev et al., 2021).
4. Role within Converter Control Architectures
The VIM synchronizer is slotted as a direct replacement for the PLL in conventional grid-following VSC designs and is agnostic to the outer-loop structure:
- Outer (system-level) loop: Computes current setpoints via – and – droop controllers, based on provided by the VIM.
- Inner (device-level) loop: Cascaded current PI control (grid-following) or voltage+current PI (grid-forming), unchanged.
- Synchronization block: VIM derives state variables and angle from , as opposed to the PLL which uses only and a PI on .
This modularity preserves existing controller infrastructure while delivering improved synchronization dynamics (Stanojev et al., 2021).
5. Stability Enhancement and Performance Studies
Linearization and eigenanalysis of the combined converter-network DAE with the VIM synchronizer underpin several key findings:
- The VIM synchronizer supports a larger droop-gain stability region than the PLL, approaching grid-forming converter performance (see Fig. 7 in (Stanojev et al., 2021)).
- Under weakening short-circuit ratio (SCR), VIM–VSCs remain stable even in very low-inertia or "very weak grids," whereas PLL–VSCs have a minimum SCR requirement of ≈1 p.u. (see Fig. 10).
- In multi-converter penetration studies, the maximum VSC share before instability rises from ≈70% (PLL) to ≈77–78% (VIM), nearly matching grid-forming limits (78.5%, see Fig. 9).
- Electromagnetic transient (EMT) simulation shows the VIM–VSC enhances damping after load- or generation-disturbances, yielding improved frequency nadir and RoCoF metrics.
These results demonstrate that VIM-based synchronization offers significantly improved small- and large-signal stability margins compared to PLL-based synchronization in low-inertia, high-penetration network settings (Stanojev et al., 2021).
6. Representative Simulation Results
Multiple EMT case studies confirm the operational and dynamic robustness of the VIM synchronizer:
| Scenario | VIM–VSC Behavior | Comparison with PLL–VSC |
|---|---|---|
| Start-up and synchronization | Synchronizes within ≈0.5 s, automatic rotor alignment | Standard transients, no lock loss |
| Set-point tracking | Clean performance on 20% power/5% voltage steps | Outer/inner loops unchanged |
| Fault ride-through | Stable under 150 ms three-phase short-circuit | PLL–VSC may lose synchronization |
| Islanding | Maintains autonomous operation after grid loss | PLL–VSC loses lock |
| Frequency disturbances | Positive damping, nadir/RoCoF improvement | PLL–VSC less effective |
Sensitivity analysis reveals that the initialization has minimal impact, and the VIM exhibits robustness under moderate parameter uncertainties and a variety of network events (Stanojev et al., 2021).
7. Tuning Guidelines and Practical Recommendations
Initial VIM parameter selection is guided by physical induction machine designs for , , , , and . Key recommendations include:
- Set slip estimator’s proportional gain as ; the derivative component requires careful tuning (e.g., Ziegler–Nichols, typically ) to prevent overshoot.
- Explore the parameter space to avoid “holes” of instability; shift towards domains with guaranteed damping.
- Implement appropriate saturation on slip estimation (), consistent with expected slip ranges such as ±0.5 Hz, to guard against measurement noise and transients.
- Validate VIM performance in EMT or hardware-in-the-loop environments, with special attention to input measurement latencies and operation under unbalanced or distorted voltages.
By following these guidelines, practitioners can achieve the desired trade-off of improved system stability, disturbance rejection, and seamless integration into existing VSC control structures (Stanojev et al., 2021).